  • This one is completely my bad; need to use it together with the ignorelb flag to override low battery signal that comes from the UPS. http://www.networkupstools.org/docs/man/apcsmart.html after changing the config to this via OMV GUI: driver = usbhid-ups port = auto ignorelb override.battery.charge.low = 30 override.battery.runtime.low = 500 it works perfectly.

  • hello, I run OMV 1.18 on a HP Microserver G8 (linux 3.2.0-4-amd64 kernel if matters). The server is connected to an APC Back-UPS CS 650EI. Installed openmediavault-nut 1.2 plugin with config: driver = usbhid-ups port = auto After that I noticed that the default value(s) for battery.charge.low =10 battery.runtime.low = 120 so added 2 lines to the config: override.battery.charge.low = 30 override.battery.runtime.low = 500 After that the new values are shown under Services/UPS/Variables, however in…